Android Code Snippet ✅ Modbus CRC-16 / CRC16 checksum function

SubName: Modbus CRC-16 is used to ensure data integrity in Modbus RTU (Remote Terminal Unit) communications.
Description: This function takes a command message Bytes and performs the necessary bitwise operations to generate a 16-bit CRC checksum, and outputs this checksum as a hexadecimal string.

The following code calculates the Modbus RTU CRC-16 (LSB-first / little-endian), the standard CRC (Cyclic Redundancy Check) used for Modbus frames.

Let's use 010107DE000A as an example to calculated it's Modbus CRC-16 value, which is 43DD.
How to use:
    Dim BC As ByteConverter
    Dim Data() As Byte = BC.HexToBytes("010107DE000A")
    Log(CalcModbusCRC(Data))
Modbus CRC-16:
Sub CalcModbusCRC(Bytes() As Byte) As String
    Dim CRCr As Int = 0xFFFF
    For i = 0 To Bytes.Length - 1
        CRCr = Bit.Xor(CRCr, Bit.And(Bytes(i), 0xFF))
        For j = 0 To 7
            If (Bit.And(CRCr, 1) = 1) Then
                CRCr = Bit.Xor(Bit.ShiftRight(CRCr, 1), 0xA001)
            Else
                CRCr = Bit.ShiftRight(CRCr, 1)
            End If
        Next
    Next
 
    'Low byte first (Modbus standard)
    Dim low As Int = Bit.And(CRCr, 0xFF)
    Dim high As Int = Bit.And(Bit.ShiftRight(CRCr, 8), 0xFF)

    Return Bit.ToHexString(high).ToUpperCase & Bit.ToHexString(low).ToUpperCase
End Sub

The full Modbus RTU frame that would be transmitted is 01 01 07 DE 00 0A 43 DD.

Here is the byte by byte Breakdown
Hex ValueDescription
01Slave Address (Unit ID): The address of the device being targeted.
01Function Code: Read Coils (Discrete Outputs).
07DEStarting Address: The address of the first coil to read (7DE hex = 2014 decimal).
000AQuantity: The number of coils to read (0A hex = 10 decimal).
43CRC Low Byte: The Least Significant Byte of the CRC.
DD
CRC High Byte: The Most Significant Byte of the CRC.


Enjoy...
 